消火栓环管管径

哪位了解消火栓系统,到底什么时候必须用DN150的环管和立管啊,消火栓规范8.1.5-3 室内消防管道管径应根据系统设计流量、流速和压力要求经计算确定;室内消火栓竖管管径应根据竖管最低流量经计算确定,但不应小于DN100。只是写了不低于DN100,而管径还应和流量、流速等等有关系,这个好计算吗,或者有没有经验说,哪些建筑必须使用DN150的消火栓立管和环管

南山桂花 | 2024-11-12 15:07
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 5

张治福 2024-11-12 16:51 00 [回复]举报

太专业,我是来搭车学习的

同同不同 2024-11-13 08:53 10 [回复]举报

这个一般由设计人员根据流量流速确定,一般在允许流速的情况下100的管径最大流量约为15L/s,超过的一般要加大管径。

南山桂花   回复: 同同不同2024-11-15 13:14

我也是设计,但是入行时间短,加上天正给排水和消火栓系统图等还没研究太深,所以我也不是很懂

0    0 [回复]举报

jinyanwu 2024-11-19 09:34 00 [回复]举报

说一下,不一定对:

假如有个DN100的管子,流速是1.5m/s,那么流量大约是12L/s,如果提高压力,流速提高到2m/s,流量大约是15.7L/s;满足一个栓流量要求;如果设计上计算的流量是30L/s,流速同样是2,那么管径大约是0.14m,工程上可以取DN150管子基本够用;

所以管径大小和压力、设计流量都有关系,压力越大,流速越大,流量就越大;

同等压力下,设计流量大,就要增加管径了。

同时水泵流量、扬程、功率等也要配套了


大悟无言 2024-11-21 15:51 00 [回复]举报

消火栓管径是在设计阶段确定的,这个由消火栓流量、消防水泵扬程、消防管道长度及水损多方面决定的。
在给定的建筑条件,即确定了消火栓流量及最不利点,管径越小,水头损失越大,水泵扬程自然就高了。
1、管径也不能太小,“8.1.8 消防给水管道的设计流速不宜大于2.5m/s”“任何消防管道的给水流速不应大于7m/s。”这也就决定了DN100的消防管道,流量宜在20L/s以内,当然按7m/s流速计算可达50L/s,但该方式会导致管网水损大,水泵扬程高,设计阶段一般不会采用。通常20L/s及以上采用DN150管道,如果单体竖向有分区或者其他高差较大的情况下,高区甚至会采用DN200的管道。
2、水泵的扬程也不能无限的大,“6.2.1 符合下列条件时,消防给水系统应分区供水:    1 系统工作压力大于2.40MPa;”、再结合8.2.3 高压和临时高压消防给水系统的系统工作压力应根据系统在供水时,可能的最大运行压力确定,并应符合下列规定“。以临高压为例,水泵扬程最高只能选用200m的。
3.上述仅讨论设计阶段的考虑,如果在实际施工过程中,建议按照图纸规格施工,如果现场条件难以满足,需选小管径,应由设计复核管网水损,水泵扬程等数据后,依变更实施。如果盲目采用小管径,会导致部分高区或者远处的消火栓栓口压力和消防水枪充实水柱,不符合“7.4.12中第2款”的规定