是不是所有的配电室都需要安装备用照明、疏散照明和疏散指示系统

根据《消防应急照明和疏散指示系统技术标准》( GB51309-2018)3.8.1配电室在发生火灾时仍需工作或值守的区域应设置备用照明、疏散照明和疏散指示标志。

但是发生火灾时,消防用电都是在配电室接出的,是不是可以理解为都需要有人去工作,因此所有的配电室都符合这条规范的描述

请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 5

赖峰 2025-02-19 10:48 10 [回复]举报

个人理解:就是所有配电室都需要符合这个规范要求

小唐12321 2025-02-19 10:53 00 [回复]举报

我理解配电房,开闭所,变压器这块,在出来就水泵房需要,主要还是你们觉得重要,每个行业不一样。

潘天坤 2025-02-19 13:22 10 [回复]举报

配电室需要设置备用照明,火灾时不需要工作和值守的配电室可以不设置疏散照明,设置气体灭火场所的配电室内的疏散通道及出口应设应急照明与疏散指示标志


建筑设计防火规范GB50016及建筑防火通用规范GB55037中都有提到:配电室以及发生火灾时仍需正常工作的消防设备房应设置备用照明,其作业面的最低照度不应低于正常照明的照度。规范正文及实施指南中关于配电室的描述没有不需要设置的前提条件,配电室中不设置备用照明可能会违反强制性条款要求


消防应急照明和疏散指示系统技术标准 GB51309中有提到“配电室等发生火灾时仍需工作、值守的区域应同时设置备用照明、疏散照明和疏散指示标志”,有些人认为发生火灾无需工作和值守的配电室可以不设置疏散照明


最后就是气体灭火系统设计规范 GB50370中有提到:设置气体灭火场所内的防护区内的疏散通道及出口应设应急照明与疏散指示标志


上述言论为根据国家规范的个人理解和交流探讨,不一定正确,也不能作为依据
有些地区技术文件可能有特别规定,建议楼主多与区域内设计、审查及验收等专家交流,具体以他们意见为准






鱼之乐 2025-02-19 13:43 00 [回复]举报

配电室主要考虑备用照明。当配电室长度>7m需要两个疏散出口时,应考虑增设出口指示标志,其他情况仅安装备用照明就好(有的配电室才2-3平方米,只有‘专家’才要求安装应急照明和疏散指示标志)

小唐12321   回复: 鱼之乐2025-02-19 14:39

大于7米哪个规范来的

0    0 [回复]举报