消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

灭火器保养

灭火器检查卡是一具一卡还是一箱一卡,有规范要求吗?

舞动的蓝焰 | 2025-02-21 09:19
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 1

萨曼岛的工程师 2025-02-21 15:03 00 [回复]举报

1.依据。《建筑灭火器配置验收及检查规范》 GB50444-2008,
5.2.1 灭火器的配置、外观等应按附录C的要求每月进行一次检查。

5.2.2 下列场所配置的灭火器,应按附录C的要求每半月进行一次检查。    

       1 候车(机、船)室、歌舞娱乐放映游艺等人员密集的公共场所;    

       2 堆场、罐区、石油化工装置区、加油站、锅炉房、地下室等场所。

5.2.3 日常巡检发现灭火器被挪动,缺少零部件,或灭火器配置场所的使用性质发生变化等情况时,应及时处置。

5.2.4 灭火器的检查记录应予保留。
2.结论。每具灭火器都应检查,因此应按照一具一卡的挂设。

关闭

关闭

手机APP下载