建筑设计防火规范 GB50016-2014(2018年版)8.5.4的条文实例

1、假设单层总面积2000平的多层丙类厂房,里面房间都是小于50平方,人员也不密集,按8.5.4条例需要设置排烟措施吗?2、建筑内部隔墙上开了窗算条文里的无窗还是有窗。


最强生物 | 2025-03-10 11:31
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 3

LHH2737 2025-03-10 13:58 10 [回复]举报

多个小于50m2的无窗房间合计面积大于200m2时,要设置排烟设施

通规8.2.5 :建筑中下列经常有人停留或可燃物较多且无可开启外窗的房间或区域应设置排烟设施:

1 建筑面积大于50m2的房间;

2 房间的建筑面积不大于50m2,总建筑面积大于200m2的区域。

(条文解释:本条规定了各类建筑中无可开启外窗的房间设置排烟设施的基本要求。这些建筑包括工业与民用建筑、独立的地下和半地下工业与民用建筑、平时使用的人民防空工程、地铁车站、隧道工程的辅助用房、城市综合管廊工程的辅助用房等。)

内部隔墙开窗但房间无外窗时,对于排烟设计算无窗房间,对于装饰装修可以按有窗房间考虑

消防资源网 2025-03-10 14:02 10 [回复]举报

8.5.4 地下或半地下建筑(室)、地上建筑内的无窗房间,当总建筑面积大于200m²或一个房间建筑面积大于50m²,且经常有人停留或可燃物较多时,应设置排烟设施。

潘天坤 2025-03-10 15:29 10 [回复]举报

请问整栋建筑一共多少人?并不是人员密集才属于人员较多


外墙上的可开启外窗才属于有窗,无外墙的窗户条件的房间在暖通专业属于无窗房间


从建规GB50016的要求来说,丙类生产场所大空间内如果无法证明不属于“人员或可燃物较多”就需要设置排烟设施,无关建筑面积要求


从建规GB50016的要求来说,丙类车间内有可开启外墙的房间当建筑面积小于300平方米,此房间可不设置排烟设施


如果丙类车间内只有一间小于50平方米的无可开启外窗的房间,那么此房间可以不设置排烟设施,当此类房间的建筑面积总和大于200平方米,那么此区域应该设置排烟设施


最后讲下,建筑防火通用规范GB55037中将丙类车间的生产场所设施排烟条件放宽了,新规定为建筑面积大于300平方米,这与建规GB50016是不一样的