既有建筑改造,共6层,改造房间在3层,改造后需占用中间部分走道做一个大房间,要在大房间两侧开门(因为房间要做屏蔽,必须封闭)。但是根据防火规范,疏散走道不应设门,但是大房间两侧办公不多且离疏散楼梯较近,是不是疏散风险较低,此方案是否成立?影响疏散吗?既有平面和改造后平面如图:


anniecool | 2025-03-12 11:48
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 4

EHS专家-DL 2025-03-12 14:34 00 [回复]举报

‌疏散距离与路径安全性‌:若改造后大房间两侧办公区人数较少(如每侧≤30人),且距疏散楼梯的水平距离≤20m(无袋形走道),可视为疏散风险较低。‌关键验证项‌:需确保大房间门开启后,疏散路径净宽度仍≥1.4m(办公建筑最低要求),且不形成新的疏散瓶颈。‌

规范豁免条件‌:根据《上海市既有建筑改造工程消防技术指南》第3.2.4条,若改造后建筑整体疏散宽度和距离仍满足原设计标准,且新增门为‌常开式甲级防火门‌(火灾时联动关闭),可申请局部豁免。


LHH2737 2025-03-13 09:26 10 [回复]举报

不成立,这样一改,左右两侧房间均只有一个安全出口

大谧   回复: LHH27372025-03-13 10:05

如果大房间两侧在通道上的门是常开防火门呢?

0    0 [回复]举报

LHH2737   回复: 大谧2025-03-13 13:50

也不可以,只有防火分区之间的分界线才可以在过道上设常开防火门,最好的做法还是拆除这两个门,可以保留门洞