一类高层住宅主卧是避难间,主卧里边的卫生间外窗也需要做乙级防火窗吗?

天涯一客 | 2025-04-02 22:16
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 3

wetom 2025-04-03 10:39 00 [回复]举报

是的,或者把卫生间门换成防火门

北极的狐2000 2025-04-06 09:03 00 [回复]举报

避难间不是不可以有可燃物吗?

vicher 2025-04-09 17:06 00 [回复]举报

此条做法依据于《建筑设计防火规范》第5.5.32条内容。个人理解,该房间定性为安全间更为贴切。

对于房间门的要求,规范规定了宜采用乙级防火门;对于外窗的要求,规范规定了耐火完整性不宜低于1.00h,另外满足此性能要求的外窗有别于防火窗;且此条非强制性条文,考虑实际日常使用,个人理解可适度放宽要求。

《住宅设计规范》第5.8.6条:厨房和卫生间的门应在下部设置有效截面积不小于0.02m的固定百叶,也可距地面留出不小于30mm的缝隙。防火门有密闭要求,用于卫生间不太妥当。