消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

审图合格查验发现的问题还能让整改吗?

防火墙上设计可开启的防火窗没有设计火警情况下自动关闭功能审图也合格了施工单位也是照图施工查验时发现此问题,施工单位以住建部门要求审图合格的图纸为验收依据,能不能要求整改?

白宝利 | 2025-04-07 09:43
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 2

EHS专家-DL 2025-04-07 10:38 10 [回复]举报

‌必须要求整改‌。尽管图纸通过审查,但防火窗缺失自动关闭功能直接违反国家标准强制性规定,存在重大消防隐患。施工单位、设计单位及审图机构均需承担相应责任,整改应以规范为最终依据,必要时可申请消防主管部门介入裁决‌。

白宝利   回复: EHS专家-DL2025-04-11 09:54

谢谢

0    0 [回复]举报

关闭

关闭

手机APP下载