消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

消防报警主机正常状态下,应该是自动还是手动?

消防规范中对各消防系统都有明确的自动状态还是手动状态的要求,

如《建筑消防设施的维护管理》中规定:

  正常工作状态下,不应将自动喷水灭火系统、防烟排烟系统和联动控制的防火卷帘等防火分隔设施设置在手动控制状态。其他消防设施及相关设备如设置在手动状态时,应有在火灾情况下迅速将手动控制转换为自动控制的可靠措施。

没有明确说明不能将火灾自动报警系统放置在手动状态。但是,有人在说火灾报警控制器的正常工作状态,就应当设置在自动状态,对此我表示疑惑,有没有人知道那条规范中对此有明确说法的


一片冰雨 | 2021-11-01 13:33
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 3

珞珞如石 2021-11-04 09:15 00 [回复]举报

5.3 消防控制室值班人员接到报警信号后,应按下列程序进行处理:     a) 接到火灾报警信息后,应以最快方式确认。     b) 确认属于误报时,查找误报原因并填写《建筑消防设施故障维修记录表》(见表B.1)。     c) 火灾确认后,立即将火灾报警联动控制开关转入自动状态(处于自动状态的除外),同时拨打“119”火警电话报警。     d) 立即启动单位内部灭火和应急疏散预案,同时报告单位消防安全责任人,单位消防安全责任人接到报告后应立即赶赴现场。

一片冰雨   回复: 珞珞如石2021-11-05 23:09

这里只是说明存在手动状态的情况,没有明确说火灾报警系统正常工作状态是手动状态!

0    0 [回复]举报

天天消防 2022-05-19 11:02 00 [回复]举报

按要求是应该一直处于自动状态才对,但现实里操作难度太大,因为万一误报,消防设施自动启动会造成损失,所以基本操作就是打在手动状态,消控室有人24小时值班,等现场确认火灾后再打成自动


关闭

关闭

手机APP下载