请教加压送风系统风管使用薄钢板法兰连接,是否可以使用弹簧夹固定?规范要求排烟风管采用薄钢板法兰连接时必须使用螺栓固定,对防烟系统是否未做要求?

请教加压送风系统风管使用薄钢板法兰连接,是否可以使用弹簧夹固定?规范要求排烟风管采用薄钢板法兰连接时必须使用螺栓固定,对防烟系统是否未做要求?麻烦各位老师解答一下。

R_MyDQ | 2022-01-15 09:25
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 2

忙里偷闲 2022-02-14 11:13 00 [回复]举报

不可以。

6.3.4 风管的安装应符合下列规定:     1 风管的规格、安装位置、标高、走向应符合设计要求,且现场风管的安装不得缩小接口的有效截面。     2 风管接口的连接应严密、牢固,垫片厚度不应小于3mm,不应凸入管内和法兰外;排烟风管法兰垫片应为不燃材料,薄钢板法兰风管应采用螺栓连接。

潘天坤 2025-02-24 14:18 00 [回复]举报

机械加压送风系统采用薄钢板法兰风管的话,就得把连接方式改成螺栓连接