排烟设施需要吗

一类高层酒店,大于100㎡的房间没有排烟设施可以吗,靠外墙有可开启的采光窗

| 2022-09-09 08:43
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 3

周家斌 2022-09-09 08:51 10 [回复]举报

靠外墙的采光窗满足自然排烟要求就可以了,

消防黄河 2022-09-11 11:34 10 [回复]举报

可开启的采光窗,按自然排烟窗口设计。校核开口有效通风面积。

感恩 2022-09-14 10:34 10 [回复]举报

按照规范要求,如果是大于100㎡的房间是需要设置排烟设施的,你这种情况,此房间为1个防烟分区,可开启外窗有效开窗面积不小于防烟分区面积的2%即可。