消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

幼儿园卫生间通风可属于消防系统啊,

幼儿园厨房及卫生间的通风是否属于消防系统,类似情况如何区分

请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 5

逍遥仙 2022-10-31 17:18 00 [回复]举报

属于专业建筑设计规范要求的通风换气要求,有别于防排烟系统。我们平常所说的通风空调系统是为满足建筑本身功能需要设置的,发生火灾时是不需要启动的。防排烟系统是为火灾时确保人员安全疏散而设置的。根据火灾发生时其起到的作用就能很好的进行区分。

周家斌 2022-10-31 22:00 00 [回复]举报

不属于消防系统,但是通风管道共用立管(主风道),每层支管要加70℃防火阀。

刘丽波 2022-11-02 06:27 00 [回复]举报

厨房本身的排油烟系统与卫生间换气系统不属于消防系统。如果厨房面积很大,有窗房间超过100平,也需要设置消防排烟系统。另外,厨房如使用燃气也会考虑事故通风。

李勤 2022-11-03 11:52 00 [回复]举报

通风肯定不属于消防系统。像建筑中排风机、排油烟风机等都不属于消防系统.(除非排风排烟合用的双速风机,图中会有说明)

潘天坤 2025-02-28 08:48 00 [回复]举报

平时通风不属于消防系统,但是要注意如果有设置防火阀的话,还要查看是否有按设计及规范要求设置防火阀。同时要注意材料的燃烧性能,绝热材料不应采用可燃材料

关闭

关闭

手机APP下载