消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

地下车库楼梯与幼儿园、老年人建筑等疏散楼梯问题?

《汽车库、修车库、停车场设计防火规范》第4.1.4条2中疏散楼梯独立设置如何理解?是否可以在首层采用防火隔墙分隔后直通室外即可,还是必须在竖向上就必须与地上楼梯就完全分开?

WR2264 | 2023-04-25 16:41
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 2

愿没有画完的图纸 2023-04-26 14:34 00 [回复]举报

上面幼儿或老年人疏散与下部地下室疏散不冲突,不存在交汇,即地下室单独通一层的室外,地上部分单独楼梯通室外,首层分隔只是起到的地下室与上部的防火分隔一说,并不是单独疏散。

dl那片海 2024-07-15 14:13 00 [回复]举报

我认为如果可以分隔就写了,没有写就说明不能像建规6.4.4那样分隔,另外可以参考图示

关闭

关闭

手机APP下载