消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

《建筑防火通用规范》有关设备房能否贴邻人员密集场所的问题

通用规范4.1.4条第1款的意思是这些设备房附设在建筑内时,当贴邻人员密集场所时应采取相应措施。这一款的意思不是可以贴邻人员密集场所吗,可是条文说明里又解释不允许贴邻,这不是自相矛盾吗?

消防网友28583 | 2023-05-17 16:17
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 3

hnlyplszq 2023-05-17 17:40 10 [回复]举报

如何证明采取的措施是正确的?

不出问题,正确。出了问题,事实证明不正确。

不贴邻。

消防网友78337 2023-05-18 08:55 10 [回复]举报

通用规范4.1.4条第一款里说了两种情况:

情况一:燃油或燃气锅炉房、可燃油油浸变压器室、充有可燃油的高压电容器室、多油开关室、柴油发电机房等具有较高火灾危险性场所独立设置在一个房子(小建筑内),这个建筑贴邻另一个建筑时,不应贴邻建筑中人员密集的场所。

情况二:上述危险性场所直接设置在一个大建筑内的一个设备房内时,设备房应设置应符合4.1.4(1、2、3)三项的要求。


整体与条文说明并不矛盾,解说很清楚,只是很难掌握。应采取防止设备用房的爆炸作用危及上一层、下一层或相邻场所的措施;措施是如何落实不清楚。

消防网友28583   回复: 消防网友783372023-05-22 10:32

你说的第二种情况就是”当受条件限制需布置在建筑内时“。4.1.4条文说明是这样写的:当受条件限制需布置在建筑内时,应按本条要求采取相应的防火措施,且不允许设置在建筑中人员聚集的场所的上面、下面或贴邻。意思不就是设备房布置在建筑内,这个房间不允许设置在建筑中人员聚集场所的上面、下面或贴邻吗?

0    0 [回复]举报

关闭

关闭

手机APP下载