仓库和车间混合设置

问题:一栋丙类厂房,一楼做仓库二楼做生产车间,那么该厂房防火措施是按照厂房还是仓库设置 还是分别设置?

13285820880 | 2023-07-22 16:53
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 7

hnlyplszq 2023-07-22 17:54 00 [回复]举报

50%对50%,整体按仓库。

同同不同 2023-07-22 19:45 00 [回复]举报

厂房仓库不应合建,满足中间仓库的除外

同同不同   回复: 同同不同2023-07-23 09:24

满足防火间距不限的也可以贴临建设

0    0 [回复]举报

13285820880   回复: 同同不同2023-07-24 16:20

不能合建的 依据是? 老厂房已经合在一起很多年了

0    0 [回复]举报

同同不同   回复: 132858208802023-07-27 14:25

建规要求厂房和仓库等需要有防火间距的

0    0 [回复]举报

阮建克18066266802   回复: 同同不同2023-08-01 22:56

可以贴邻,但是不可以合建(中间仓库除外)。

0    0 [回复]举报

消防君 2023-07-25 13:55 10 [回复]举报

建筑要求和消防设施整体建议按照仓库要求建设。一般楼上做仓储会比较好,利于异常情况员工疏散。

至于防火,除了设置防火墙,层间还要设置防火挑檐分隔,楼板需确认并加强耐火等级。排烟设施不通用,分开设置。物流通道设置在户外,人员通行如有必要可设防火隔间。