消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

消防取水口

消防水池一定要设置消防取水口吗?公司消防水池高度4米,其中地面以下1.5米、地上2.5米。如果设置消防取水口,势必消防水池内消防水漏去大半! 这是强规吗?

远古鱼龙 | 2023-07-25 08:38
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 7

安洪全 2023-07-25 12:12 00 [回复]举报

取水栓口不一定在消防水池储水面至上啊。


远古鱼龙   回复: 安洪全2023-07-25 13:12

谢谢!这个取水口倒是第一次看到,这个与室外栓取水有啥区别?

0    0 [回复]举报

安洪全   回复: 远古鱼龙2023-07-25 14:38

0    0 [回复]举报

周家斌 2023-07-26 08:40 10 [回复]举报

消防水池只有存储室外消防用水时候,才设置取水口(井)

远古鱼龙   回复: 周家斌2023-07-26 13:20

就是说用于消防、生产合用消防水池不用设置取水口吗?

0    0 [回复]举报

周家斌   回复: 远古鱼龙2023-07-26 13:44

不是,市政给水不满足两路供水能力的情况下,消防水池需要储存室外用水量的。

1    0 [回复]举报

远古鱼龙   回复: 周家斌2023-07-27 13:09

谢谢周老师1我们不是市政供水,是企业内部消防供水,是满足双路供水涉及要求,并且是三个2000方总共6000方的消防水池!

0    0 [回复]举报

关闭

关闭

手机APP下载