请教!为什么没有说明甲乙与丙丁戊之间的防火间距最少是多少?

两座一、二级耐火等级的厂房,当相邻较低一面外墙为防火墙且较低一座厂房的屋顶无天窗,屋顶的耐火极限不低于1.00h,或相邻较高一面外墙的门、窗等开口部位设置甲级防火门、窗或防火分隔水幕或按本规范第6.5.3条的规定设置防火卷帘时,甲、乙类厂房之间的防火间距不应小于6m;丙、丁、戊类厂房之间的防火间距不应小于4m。

消防网友80490 | 2021-02-19 21:28
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 4

消防小陈 2021-02-20 09:43 00 [回复]举报

建筑设计防火规范3.4.1条表写明防火间距的。

飞翔的心 2021-02-20 12:01 00 [回复]举报

个人理解,甲乙与丙丁戊之间的防火间距也不应小于6m。

消防网友51935 2021-02-20 22:13 00 [回复]举报

3.4.1已说明甲乙与丙丁戊之间的防火间距

逍遥无悔 2021-02-22 09:40 00 [回复]举报

没有特殊条件的甲乙类和丙丁戊的防火间距具体在防火规范的表中,没有提到的各种甲级防火门,防火水幕分隔,没提到甲乙与丙丁戊之间,即按照6米从严