消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

【问】请教大家,室内消火栓按钮,是必须设置的吗?

我们有个项目,建筑内不需要设火灾自动报警系统,然后室内消火栓按钮也不设,这样可以吗?通过消防水泵出水干管的低压压力开关启泵。

消防资源网 | 2024-06-03 17:39
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 3

潘天坤 2024-06-03 18:22 20 [回复]举报

1、《民用建筑电气设计标准》(GB51348-2019)第13.4.7条规定:设置消防控制室的公共建筑,消火栓旁应设置消火栓按钮;设置消防控制室的54米及以上住宅建筑,消火栓旁应设置消火栓按钮;当住宅建筑群有54米及以上住宅建筑,亦有27米以下住宅建筑时,27米以下住宅建筑可不设消火栓按钮。

2、没有设计火灾自动报警系统,理论上是不遵照火灾自动报警系统的规范,这边条文说明有引用内容,就蛮附上参考交流。

《火灾自动报警系统设计规范》(GB50116-2013)第4.3.1条的条文说明提及:稳高压系统中,虽然不需要消火栓按钮启动消防泵,但消火栓按钮给出的使用消火栓位置的报警信息是十分必要的,因此稳高压系统中,消火栓按钮也是不能省略的。当建筑物内无火灾自动报警系统时,消火栓按钮用导线直接引至消防泵控制箱(柜),启动消防泵。

3、没有设置火灾自动报警系统,一般没有消防控制室,但是要考虑其他系统需要利用既有消防控制室这种情况,这个特殊情况不知道如何执行。其余情况,按照相关规范要求可以不设置消火栓按钮。当然最好参照地区技术文件,看看有没有对此做出特别要求。

夏至930   回复: 潘天坤2024-10-22 11:42

问一下,就如果没有火灾自动报警系统时,消火栓按钮用导线直接接到消防泵控制箱上吗?串联?

0    0 [回复]举报

同同不同 2024-06-05 20:53 00 [回复]举报

按各地相关规定,譬如山东江苏可不设置

关闭

关闭

手机APP下载