消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

消防通规4.2.6条的“任何开口”包括暖通、电气管道吗?

4.2.6 仓库内的防火分区或库房之间应采用防火墙分隔,甲、乙类库房内的防火分区或库房之间应采用无任何开口的防火墙分隔。

请问:这里面的“任何开口”包不包含6.3.4条里面的 “电气线路和各类管道”呢,目前有项目消防审查专家提到了这个问题,专家认为是不包含的。他们认为甲乙类库房上任何管道洞口都不允许穿过,即使做了防火封堵及耐火措施。

小猪佩佩奇 | 2024-06-22 16:51
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 5

黄-江西省景德镇市 2024-06-24 05:37 00 [回复]举报

应按审查专家意见执行。

LHH2737 2024-06-24 09:16 00 [回复]举报

建规说甲、乙类仓库内防火分区之间的防火墙不应开设门、窗、洞口;通规改为了采用无任何开口的防火墙,很明显是更严了,那就是电气线路和管道也不能穿

phone0224 2024-06-24 09:55 00 [回复]举报

如果是管道横向穿越甲乙类库房的防火分区是不允许的。

香.香 2024-06-24 10:13 00 [回复]举报

甲乙库房的防火分区之间应采用防火墙分隔且防火墙上不应开设门、窗、洞口。这句指的是甲乙仓库的分隔只能是防火墙不能采用其它方式代替,它着重强调的是分隔的方式。至于电器管道能不能穿防火墙?是可以穿的但是要采用防火材料封堵且用不同的穿管材料对封堵材料也是有要求的。可燃气体、甲乙丙可燃液体是严禁穿防火墙的,排气管道不应穿。你提及的无任何开口主要强调的是分隔方式和不开设门窗洞。个人认为,仓库分隔看分隔方式是否满足规范要求,防火墙能否穿管道还得看防火墙 的设置要求,不能够混淆。

最帅游客 2024-06-24 12:05 00 [回复]举报

啥口都不能开,甲乙类已经很危险了……

关闭

关闭

手机APP下载