消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

防烟分区用侧吸和底吸两种方式,怎么计算?

因为现场设备及层高问题,所在防烟分区需要设置两种排烟口,会分管设置,V=15000,想知道侧吸和底吸应该怎么计算,设置几个风口,谢谢

来福 | 2024-07-22 11:47
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 8

@mad 2024-07-22 13:51 00 [回复]举报

条件不足,无法判断需要设几个排烟口。项目所属省市,房间净高,有无喷淋,使用功能,风口大小及距墙距离。条件充足才能校核单个排烟口最大允许排烟量。

来福   回复: @mad2024-07-22 14:13

广州,净高为2.9,有喷淋,商业用途,排烟口做300*250的,侧吸大于两倍当量直径,底吸小于(要跟着天花设计走)

0    0 [回复]举报

潘天坤   回复: 来福2024-07-22 20:50

按照楼主的描述计算了下,如果需要考虑最大允许排烟量那么烟层厚度取0.55米(排烟口位置系数取1,MW取3,燃料面到烟层底部的高度取1.45)的时候,单个排烟口最大允许排烟量为4186m³/h(0.3*0.25的排烟口,如果是普通百叶排烟量是3375m³/h,如果是板式排烟口的排烟量是2700m³/h)

挺多人认为净高不大于3米的场所不考虑单个排烟口最大允许排烟量这个要求,不知道楼主所在地区是怎么要求的,建议楼主多与区域内设计、审查及验收专家交流,具体以他们意见为准

0    0 [回复]举报

潘天坤 2024-07-22 20:34 00 [回复]举报

一般来说,单个排烟口最大允许排烟量可以通过查表法,也可以通过计算得出

烟层厚度(排烟系统吸入口最低点之下烟气层厚度)、排烟位置系数(当风口中心点到最近墙体的距离≥2倍的排烟口当量直径时:γ取1.0;当风口中心点到最近墙体的距离< 2倍的排烟口当量直径时:γ取0.5;当吸入口位于墙体上时,γ取0.5)、火灾热释放速率、是否设置自动灭火设施等均会影响单个排烟口最大允许排烟量的数据

根据GB51251烟标相关要求,侧排的烟层厚度为排烟口中心距挡烟垂壁局里,侧排相比上排或者下排会减小烟层厚度,从而加大单个排烟口最大允许排烟量的数据

不过业内挺多人认为净高不大于3米的场所不考虑单个排烟口最大允许排烟量这个要求,不知道楼主所在地区是怎么要求的,建议楼主多与区域内设计、审查及验收专家交流,具体以他们意见为准
上述为根据国家规范的个人理解,不一定正确,有些地区技术文件可能有特别规定,建议结合地区技术文件和地区设计、审查、验收专家们的意见综合考虑


来福   回复: 潘天坤2024-07-23 11:37

好的,感谢

0    0 [回复]举报

LHH2737 2024-07-23 09:28 00 [回复]举报

不管侧排,底排还是顶排,风口计算公式都是:该防烟分区每小时排烟量量*1.2/3600/10,需要设置几个风口应查建筑防烟排烟系统技术标准附录B

来福   回复: LHH27372024-07-23 11:38

好的,谢谢

0    0 [回复]举报

潘天坤   回复: LHH27372024-07-23 12:23

板式排烟口系数取1,其他有遮挡系数的百叶应该适当考虑遮挡系数比较合理

同时除了查表,还可以通过计算复核

0    0 [回复]举报

关闭

关闭

手机APP下载