请问一下排烟口的相关问题。

厂房内设置吊顶净高为2.8米的房间内,防烟分区面积150平方米,设置一个600*1200的排烟口,是否还需要考虑单口排烟风量? 采用计算软件复核后,房间内风量为15000,挡烟垂壁高度为0.5米·,烟气厚度也按0.5米,单口排烟量为2488,所需排烟风口数量为7个。请问一下各位大佬净高在小于三米或者等于三米的情况下,是否还需要考虑单个排烟风口的最大风量?如果不考虑 是否可以只做一个600*1200的排烟风口?

WeiHL | 2024-07-23 21:46
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 5

潘天坤 2024-07-24 10:01 20 [回复]举报

业内挺多人认为空间净高不大于3米的场所,可以不考虑单个排烟口最大允许排烟量,不知道楼主的地区是否有文件特别规定,建议楼主多与区域内设计、审查及验收专家交流,具体以他们意见为准

设置自喷的情况下,热释放速率为2.5,烟层厚度0.5米,燃料面到烟层底部的高度为1.4米,排烟位置系数取1,此情况计算得出的单个排烟口最大允许排烟量为3237m³/h,此时需要5个排烟口。是否考虑增大挡烟垂壁高度来加大烟层厚度,来减小排烟口数量?烟层厚度达到0.6米时,挡烟垂壁距地高度为2.2米,单个排烟口最大允许排烟量为5105m³/h,此时需要3个排烟口。还可以考虑设置开孔率大于25%的通透性吊顶,此时挡烟垂壁可以设置在吊顶内,烟层厚度可以增大。

上述为根据国家规范的个人理解,不一定正确,有些地区技术文件可能有特别规定,建议结合地区技术文件和地区设计、审查、验收专家们的意见综合考虑

消防网友68723 2024-07-24 10:46 00 [回复]举报

GB51251,对排烟口最大排烟量有要求

草鱼 2024-08-02 08:33 00 [回复]举报

我想借楼咨询一个问题,规范明确表明3米以下的,最小清晰高度可以按照净高的1/2计算,但是通规又明确指出,疏散高度不得小于2.1m,那么这个1/2的清晰高度是否还有意义,挡烟垂壁最低只能做到2.1m,那储烟仓是否能按照1/2去计算

WeiHL   回复: 草鱼2024-08-02 09:22

个人感觉房间内部可以按1/2去算,像走道或者其他防烟分区采用挡烟垂壁分隔的就只能按实际储仓计算

0    0 [回复]举报

潘天坤   回复: 草鱼2024-09-12 15:58

走道和小于3米的场所的挡烟垂壁确实比较麻烦,不知道通过设置通透性吊顶能不能尽量满足要求

计算肯定是按照二分之一考虑,如果真要考虑设计清晰高度,可能确实会与规范冲突

0    0 [回复]举报