消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

各防烟分区支管管径、排烟口需要按照风机风量核算风速吗?

一个项目,审图老师认为:当火灾确认后, 担负两个及以上防烟分区的排烟系统,应仅开启着火防烟分区排烟系统的排烟阀或排烟口。其他防烟分区的排烟阀或排烟口均应关闭。所以一个防烟分区风支管管径、排烟口需要按照排烟风机风量核算风速,请问这样的话是不是整个建筑内风管及风口就是一个规格型号了?合理吗?

lilimin | 2021-03-29 10:40
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 4

消防网友62851 2021-03-30 10:05 00 [回复]举报

防烟分区大小不一样,室内净高也可能不一样,排烟量不一样,那对应着排烟口和排烟风管不一定是同一规格。

排烟规范第4.6.4条1:当系统负担具有相同净高场所时,对于建筑空间净高大于6m的场所,应按排烟量最大的一个防烟分区的排烟量计算;对于建筑空间净高为6m及以下的场所,应按同一防火分区中任意两个相邻防烟分区的排烟量之和的最大值计算。

lilimin   回复: 消防网友628512021-04-09 10:07

因为审图理解火灾时只是开启火灾防烟分区的排烟口,但是风机风量是固定的,这样风口风速会超10m/s。不满足规范要求。

0    0 [回复]举报

汪汪 2021-04-01 15:23 00 [回复]举报

斗胆回答:设计时候按同一时间发生一处火灾考虑的话,排烟对应也只需要开启一个防烟分区内的排烟阀和排烟口即可!所以多个防烟分区的风口和风管规格型号都是相同的,按《建筑防烟排烟系统技术标准》选择风机排烟量。

mshm 2023-12-16 18:05 00 [回复]举报

条文解释4.6.4说的很清楚,任意一段风管段的风量,取其负担的下游几个防烟分区中相邻的两个最大防烟分区风量之和

关闭

关闭

手机APP下载